				Home Electrical Question
			 
 
			
			I know there are a few electricians on here so I thought I'd post up:
 I have a room air conditioner that pulls 12A @ 110. I ran a dedicated outlet for it using 12ga romex (just in case) and a 15A breaker that pulls off of a 30A subpanel.
 
 For most of the day the A/C unit runs fine, but occasionally I blow the breaker and I don't know why. The unit is only supposed to pull 12A, not enough to blow the 15A breaker. I've got a 20A breaker ready to go but I don't want to put it in if it's going to be a band aid to a bigger problem.
 
 Any ideas?
 |  
	|   |   |  
	
		
	
	
	
		|  07-06-2008, 02:13 PM | #2 |  
	| 15 Second Club 
				 
                                        
				Join Date: Aug 2005 Location: Beaufort SC 
					Posts: 1,165
				     
                                    
                                 | 
			
			whats it draw for when it first kicks on the compressor? cuz thats gonna be the biggest draw.
		 
				__________________2005 Colorado Z71 - Supermod tuned, SuperSparkz, Resonator delete, SuperMod PTB
 
 next up - 3" lift, Gutted cat/retune/muffler
 
 Past Toys:
 1983 Trans AM, 1988 Trans AM, 2001 Dodge Ram 1500 Off-Road, 1986 Camaro IROC, 1984 Chevy K10 lifted, 1988 Mustang GT, 2006 Silverado 2500HD
 |  
	|   |   |  
	
		
	
	
	
		|  07-06-2008, 02:32 PM | #3 |  
	| Ayatollah of Rock N Rolla / Admin 
				 
                                        
				Join Date: Mar 2006 Location: Parts Unknown 
					Posts: 12,573
				     
                                    
                                 | 
			
			
	Quote: 
	
		| 
					Originally Posted by trashman01  whats it draw for when it first kicks on the compressor? cuz thats gonna be the biggest draw. |  12A.
		 |  
	|   |   |  
	
		
	
	
	
		|  07-06-2008, 02:34 PM | #4 |  
	| 
				 
                                        
				Join Date: Jun 2007 Location: Arm pit of the world... NJ 
					Posts: 2,677
				     
                                    
                                 | 
			
			Bill, you're right at the 80% rating of a 15 amp circuit. I'd step up to the 20A.
		 
				__________________John
 |  
	|   |   |  
	
		
	
	
	
		|  07-06-2008, 02:37 PM | #5 |  
	| Ayatollah of Rock N Rolla / Admin 
				 
                                        
				Join Date: Mar 2006 Location: Parts Unknown 
					Posts: 12,573
				     
                                    
                                 | 
			
			
	Quote: 
	
		| 
					Originally Posted by Featherburner  Bill, you're right at the 80% rating of a 15 amp circuit. I'd step up to the 20A. |  Yeah, I have been reading up on that. Looks like 20A will be the way to go.
		 |  
	|   |   |  
	
		
	
	
	
		|  07-06-2008, 02:41 PM | #6 |  
	| Power Member 
				 
                                        
				Join Date: Oct 2007 Location: Milford NJ 
					Posts: 1,526
				     
                                    
                                 | 
			
			
	Quote: 
	
		| 
					Originally Posted by Featherburner  Bill, you're right at the 80% rating of a 15 amp circuit. I'd step up to the 20A. |  
exactly right.
 
the issue is probably this; when the air turns on the compressor starts, its a motor load and when motors start they draw and VERY large amount of current during the initial start-up, then settle back to the running load.  This is why the 15A breaker trips sometimes.  The 20A breaker will cause no issues, just dont overload the 30 sub-panel.
 
And like featherburner said, a circuit it not supposed to draw more that 80% of its ampacity on a continuous load, like an air conditioner.  It can actually degrade the breaker and other components due to excessive heat. 
________
Coach purses 
				 Last edited by //<86TA>\\; 05-04-2011 at 06:51 PM.
 |  
	|   |   |  
	
		
	
	
	
		|  07-07-2008, 04:14 PM | #7 |  
	| 
				 
                                        
				Join Date: Feb 2005 Location: Little Egg Harbor NJ 
					Posts: 1,175
				     
                                    
                                 | 
			
			use this simple rule of thumb- if you need 12 gauge wire, you need a 20 amp breaker. if you use 14 gauge wire, use a 15 amp breaker.
		 
				__________________2011 Camaro 1SS Cyber Grey Metallic
 2005 Silverado
 |  
	|   |   |  
	
		
	
	
	
		|  07-07-2008, 04:18 PM | #8 |  
	| Ayatollah of Rock N Rolla / Admin 
				 
                                        
				Join Date: Mar 2006 Location: Parts Unknown 
					Posts: 12,573
				     
                                    
                                 | 
			
			
	Quote: 
	
		| 
					Originally Posted by nj85z28  use this simple rule of thumb- if you need 12 gauge wire, you need a 20 amp breaker. if you use 14 gauge wire, use a 15 amp breaker. |  True. I am aware of this. I didn't think I "needed" the 12 gauge wire, but I used it as overkill. Thanks though!
 
I was not aware of the fact that a 12A draw is "close enough" to a 15A breaker to trip it.
		 |  
	|   |   |  
	
		
	
	
	
		|  07-07-2008, 04:23 PM | #9 |  
	| 
				 
                                        
				Join Date: Feb 2005 Location: Little Egg Harbor NJ 
					Posts: 1,175
				     
                                    
                                 | 
			
			the only thing you really use a 15 amp breaker for in a house is lighting and some light duty receptacles. at least its an easy fix and you dont have to rip the wire back out. good luck
		 
				__________________2011 Camaro 1SS Cyber Grey Metallic
 2005 Silverado
 |  
	|   |   |  
	
		
	
	
	
		|  07-07-2008, 09:21 PM | #10 |  
	| Power Member 
				 
                                        
				Join Date: Oct 2007 Location: Milford NJ 
					Posts: 1,526
				     
                                    
                                 | 
			
			
	Quote: 
	
		| 
					Originally Posted by WildBillyT  I was not aware of the fact that a 12A draw is "close enough" to a 15A breaker to trip it.
 |  
like we said, 12A will not trip a breaker, but its the starting current spike of the AC that will do it.  Its probably upwards of 25 amps for a split second. 
________
Marijuana medical 
				 Last edited by //<86TA>\\; 05-04-2011 at 06:52 PM.
 |  
	|   |   |  
	
		
 
  
	
	
	
	
	| 