Ok so this is the first house I've had central air in and I like it but I have a question or two. How long should my unit run at a time? It runs about 12 to 15 minutes at a time this weekend and kicks off. But is only off maybe 5-10 before running another 15. Is this normal? I don't want my electric bill to be nuts if it doesn't have to be.
__________________
Formerly known as blk95formula
86t/a_ram_air on TGO
2018 Silverado 1500
|
|
|
05-28-2012, 09:58 PM
|
#2
|
Join Date: Apr 2006
Location: Point Pleasant
Posts: 1,809
|
Whats it set at? With the temps at 80-90 this weekend you'll be in for a bill if your trying to get lower than 75.
Im in an apartment with central air/forced hot air. This weekend it was 15mins on 45mins off keeping the place at 74.
__________________
-Vinnie
94 2wd SBSC Gmt400. 330CI LSX, Fast 102, Trickflow 205s, close ratio nv3500, 4.30/trutrac.
|
|
|
05-28-2012, 10:03 PM
|
#3
|
Ayatollah of Rock N Rolla / Admin
Join Date: Mar 2006
Location: Parts Unknown
Posts: 12,573
|
A lot of variables. Depends on how lossy the house is.
|
|
|
05-28-2012, 10:35 PM
|
#4
|
Join Date: May 2010
Location: Brick, NJ
Posts: 1,868
|
Its a fairly small 2 bedroom ranch with a "office". I have thermo set on 70 partly because of the dogs. Even as we speak its 10 minutes on for every 5 off
__________________
Formerly known as blk95formula
86t/a_ram_air on TGO
2018 Silverado 1500
|
|
|
05-28-2012, 10:55 PM
|
#5
|
Co-Founder / Site Admin
Join Date: Jul 2004
Location: Ewing, NJ
Posts: 22,476
|
Every few degrees you can raise that will make a big difference in your electric bill. JMHO, but the dogs should be perfectly comfortable inside the house at 74-75.
- Justin
__________________
1999 Camry - Beigemobile DD
2002 Suburban - Wife's DD
2004 Grand Cherokee - Not running / Project / Selling?
|
|
|
05-28-2012, 11:33 PM
|
#6
|
Join Date: Jul 2009
Location: barnegat nj
Posts: 1,340
|
I have found that maintaining 75-76 degrees has given me the best results on my electric bill. but every house is different. If your losing the cool due to poor windows and insulation, than the longer the unit is going to run and cycle on/off more frequently to maintain the temp you desire.
p.s. fans do help. fans produce a "wind chill" effect, and depending on your vent locations (ceiling or floor) can help move the cool air through the house.
__________________
Quote:
Originally Posted by SRGN
I never pulled into the staging beams at the track and saw a dyno in the other lane.
|
South Jersey Racecraft
Last edited by S.J.SLEEPER; 05-28-2012 at 11:35 PM.
|
|
|
05-29-2012, 07:31 AM
|
#7
|
Join Date: May 2010
Location: Brick, NJ
Posts: 1,868
|
Most vents are on the cieling with the exception of 1 which is in a wall. It just seems like if its off 5 minutes its on 10. I bumped it up to 72 to see if that makes it any different
__________________
Formerly known as blk95formula
86t/a_ram_air on TGO
2018 Silverado 1500
|
|
|
05-29-2012, 07:38 AM
|
#8
|
Join Date: Jun 2011
Location: Morris county
Posts: 155
|
I have a boxer and if it goes above 85 outside she starts to huff and puff like she's having trouble breathing. I just turn the air on slightly to get the humidity out of the house and she does fine inside.
__________________
There's things about me you wouldn't understand, things you couldn't understand, things you SHOULDN'T understand
Last edited by OG; 05-29-2012 at 07:40 AM.
|
|
|
05-29-2012, 07:48 AM
|
#9
|
Join Date: May 2010
Location: Brick, NJ
Posts: 1,868
|
yeah but 80 in the house isn't all that comfortable for me either
__________________
Formerly known as blk95formula
86t/a_ram_air on TGO
2018 Silverado 1500
|
|
|
05-29-2012, 08:05 AM
|
#10
|
Join Date: Feb 2005
Location: west orange nj
Posts: 2,415
|
everyone i know puts the ac on between 72 and 76 i helped a friend install ac units when he needs help
|
|
|
05-29-2012, 09:25 AM
|
#11
|
Join Date: Mar 2007
Location: NJ
Posts: 540
|
I usually run mine around 74, anything above that and it gets stuffy in the house.
I had all kinds of issues after I first moved in. The house was built in 1953 and it had AC installed in 2004 and it's all stuffed in the attic. Someone did a lousy install and I had air leaks at all of the vents and even at the blower case, they were barley even bolted together. On really hot days the system struggled to keep the house at 76, it ran all day and did not shut off at all.
Still not the way I would like it but its fixed.
|
|
|
05-29-2012, 10:24 AM
|
#12
|
Join Date: May 2010
Location: Brick, NJ
Posts: 1,868
|
Ill leave it at 72 for now and after I get home from work tonight ill pay attention to it. If the thermo had a 1 or 2 degree degree swing it would probobly run less
__________________
Formerly known as blk95formula
86t/a_ram_air on TGO
2018 Silverado 1500
|
|
|
05-29-2012, 10:30 AM
|
#13
|
Join Date: Jun 2007
Location: Arm pit of the world... NJ
Posts: 2,677
|
Quote:
Originally Posted by greenformula92
Ill leave it at 72 for now and after I get home from work tonight ill pay attention to it. If the thermo had a 1 or 2 degree degree swing it would probobly run less
|
Is it a digital thermostat? It may be set on the wrong setting causing the a/c to run sooner than it should.
__________________
John
|
|
|
05-29-2012, 11:00 AM
|
#14
|
Join Date: May 2010
Location: Brick, NJ
Posts: 1,868
|
It is a digitall but it basically has no options. It doesn't have scedules or anything, it just has temp adjust and cool/heat on off selector
__________________
Formerly known as blk95formula
86t/a_ram_air on TGO
2018 Silverado 1500
|
|
|
05-29-2012, 11:04 AM
|
#15
|
Ayatollah of Rock N Rolla / Admin
Join Date: Mar 2006
Location: Parts Unknown
Posts: 12,573
|
I think it's called an anticipator circuit and you can only get to it via the rear of the stat.
Do you have an attic with an attic fan?
|
|
|
05-29-2012, 12:12 PM
|
#16
|
Join Date: May 2010
Location: Brick, NJ
Posts: 1,868
|
Quote:
Originally Posted by WildBillyT
I think it's called an anticipator circuit and you can only get to it via the rear of the stat.
Do you have an attic with an attic fan?
|
Negative, but all my HVAC stuff is up there minus the a/c unit which is on the side of the house on a platform
__________________
Formerly known as blk95formula
86t/a_ram_air on TGO
2018 Silverado 1500
|
|
|
05-30-2012, 07:56 AM
|
#17
|
Meet Coordinator
Join Date: Jan 2008
Location: brick/pt. pleasant beach
Posts: 19,368
|
Quote:
Originally Posted by WildBillyT
I think it's called an anticipator circuit and you can only get to it via the rear of the stat.
Do you have an attic with an attic fan?
|
I do, please tell me moar. First rodeo.
|
|
|
05-30-2012, 08:06 AM
|
#18
|
Ayatollah of Rock N Rolla / Admin
Join Date: Mar 2006
Location: Parts Unknown
Posts: 12,573
|
Quote:
Originally Posted by sweetbmxrider
I do, please tell me moar. First rodeo.
|
About the attic fan or the anticipator?
|
|
|
05-30-2012, 08:25 AM
|
#19
|
Meet Coordinator
Join Date: Jan 2008
Location: brick/pt. pleasant beach
Posts: 19,368
|
Attic fan, feels like indiana jones.
|
|
|
05-30-2012, 09:37 AM
|
#20
|
Ayatollah of Rock N Rolla / Admin
Join Date: Mar 2006
Location: Parts Unknown
Posts: 12,573
|
Quote:
Originally Posted by sweetbmxrider
Attic fan, feels like indiana jones.
|
A good running attic fan that turns on at the proper temperature will extract heat out of your roof and help keep things cool. Over time the bearings go bad and they make noise/spin slower so they don't work as well. An added bonus is that it helps with roof life.
|
|
|
05-30-2012, 09:57 AM
|
#21
|
Meet Coordinator
Join Date: Jan 2008
Location: brick/pt. pleasant beach
Posts: 19,368
|
Ok I get the concept. The ac guy said to set it for around 80* (its thermostat controlled) so all that hot air isn't pushing against the bedroom ceilings. The fan works great, it will pull the doors open if they are cracked. Its an old belt driven unit so I think it was made back when America gave a **** and should outlast me.
|
|
|
05-30-2012, 10:26 AM
|
#22
|
Meet Coordinator
Join Date: Jan 2008
Location: brick/pt. pleasant beach
Posts: 19,368
|
Turns out its a whole house fan for pulling air through the house on nice spring/fall days.
|
|
|
05-30-2012, 11:19 AM
|
#23
|
Mongo the Meet Coordinator
Join Date: May 2008
Posts: 16,938
|
Quote:
Originally Posted by sweetbmxrider
Turns out its a whole house fan for pulling air through the house on nice spring/fall days.
|
Why was I aware of this but you were not?
__________________
Quote:
Originally Posted by KirkEvil
repo bigals turd gen and part it out to a loving home
|
|
|
|
05-30-2012, 11:31 AM
|
#24
|
Meet Coordinator
Join Date: Jan 2008
Location: brick/pt. pleasant beach
Posts: 19,368
|
My parents use window units? I dono, just trying to be energy efficient. I like not paying electric bills doe
|
|
|
05-30-2012, 11:33 AM
|
#25
|
Mongo the Meet Coordinator
Join Date: May 2008
Posts: 16,938
|
Quote:
Originally Posted by sweetbmxrider
My parents use window units? I dono, just trying to be energy efficient. I like not paying electric bills doe 
|
Nah I mean like Kirk mentioned it to me at some point before.